Fire alarm device labeling

Status
Not open for further replies.

GrayHair

Senior Member
Location
Nashville, TN
I've been retired for several years and no longer keep up with NFPA 72, that said, I know of no such requirement. I visibly labeled all devices with Panel/Sub-panel, Loop/Zone and Device. Addressable panels usually include the device address as part of alarm/trouble history and visibly labeled devices will speed troubleshooting. Also nice for testing. :)

This was a carry-over from conventional systems where knowing the wiring sequence would allow you to locate a single fault never having to check more than 50% +1 devices.
 

iwire

Moderator
Staff member
Location
Massachusetts
Can someone tell me if there is a code requiring
installing address labels on addressable fire alarm devices? I thought I saw
this once but am having trouble locating it again

I do not believe there is such a code requirement.


But we do it because the fire department asks for it.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I do not believe there is such a code requirement.


But we do it because the fire department asks for it.

Yeah, same here. I just hate getting the "stink eye" from the AHJ, then he really starts checking things out.
 