elecold Member Jul 30, 2018 #1 Can die cast MC connectors be used with fire alarm cable? Or does it have to be a steel MC connector?
Can die cast MC connectors be used with fire alarm cable? Or does it have to be a steel MC connector?
gadfly56 Senior Member Location New Jersey Occupation Professional Engineer, Fire & Life Safety Jul 30, 2018 #2 elecold said: Can die cast MC connectors be used with fire alarm cable? Or does it have to be a steel MC connector? Click to expand... The national codes are silent on this. You should check to see if your locality has any special requirements, e.g. New York City, Chicago.
elecold said: Can die cast MC connectors be used with fire alarm cable? Or does it have to be a steel MC connector? Click to expand... The national codes are silent on this. You should check to see if your locality has any special requirements, e.g. New York City, Chicago.
elecold Member Jul 30, 2018 #3 gadfly56 said: The national codes are silent on this. You should check to see if your locality has any special requirements, e.g. New York City, Chicago. Click to expand... Thanks for your time Do you know if Massachusetts requires steel mc connectors?
gadfly56 said: The national codes are silent on this. You should check to see if your locality has any special requirements, e.g. New York City, Chicago. Click to expand... Thanks for your time Do you know if Massachusetts requires steel mc connectors?
peter d Senior Member Location New England Jul 30, 2018 #4 Where are you located? In Rhode Island, only steel MC and EMT connectors are allowed per statewide code. Mass. has no state code that I'm aware of, but some towns might. Check with your local fire alarm official.
Where are you located? In Rhode Island, only steel MC and EMT connectors are allowed per statewide code. Mass. has no state code that I'm aware of, but some towns might. Check with your local fire alarm official.