Can you run Fire Alarm riser cable through floors? Or do you have to change to conduit? 6 story building
 
Can you run Fire Alarm riser cable through floors? Or do you have to change to conduit? 6 story building

If you are using FPLR cable then of course you can. Same for FPLP, as the hierarchy goes FPL>>FPLR>>FPLP. Southwire's Red Alert® product would be ideal.

All of the above is subject to modification by any local ordinances or contract requirements.
 