1 101010 Senior Member Apr 19, 2018 #1 Can you run Fire Alarm riser cable through floors? Or do you have to change to conduit? 6 story building
Can you run Fire Alarm riser cable through floors? Or do you have to change to conduit? 6 story building
gadfly56 Senior Member Location New Jersey Occupation Professional Engineer, Fire & Life Safety Apr 19, 2018 #2 101010 said: Can you run Fire Alarm riser cable through floors? Or do you have to change to conduit? 6 story building Click to expand... If you are using FPLR cable then of course you can. Same for FPLP, as the hierarchy goes FPL>>FPLR>>FPLP. Southwire's Red Alert® product would be ideal. All of the above is subject to modification by any local ordinances or contract requirements.
101010 said: Can you run Fire Alarm riser cable through floors? Or do you have to change to conduit? 6 story building Click to expand... If you are using FPLR cable then of course you can. Same for FPLP, as the hierarchy goes FPL>>FPLR>>FPLP. Southwire's Red Alert® product would be ideal. All of the above is subject to modification by any local ordinances or contract requirements.