Does anyone know if Notification Appliances have to be included in all new construction? I checked the International Building Code and it is very vague.
In the IBC, Section 907.2, it says to install a fire alarm system and occupant notification per 907.2.1 - 907.2.23.
So if you have an occupancy that needs a fire alarm system listed in those sections, then you need notification that is described in 907.5