lowvolts1224
New member
- Location
- Florida
Hello,
Recently, there has been a question regarding the interpretation of the NFPA 72 test methods. The NFPA 72 "Secondary Power Supply" test methods state:
General alarm systems shall be operated for a minimum of 5 minutes, and emergency voice coummunications systems shall be operated for a minimum of 15 minutes.
I have been told by another technician that if a battery tester is used, as is allowed by the exceptions under "Batteries -- General Tests" section, that it is not necessary to sound the alarm for 5 minutes/15 minutes as is called for in the Secondary Power Supply section. Can anyone tell me if this is correct? My state is currently under the 2012 edition of the NFPA 72.
Thanks
Recently, there has been a question regarding the interpretation of the NFPA 72 test methods. The NFPA 72 "Secondary Power Supply" test methods state:
General alarm systems shall be operated for a minimum of 5 minutes, and emergency voice coummunications systems shall be operated for a minimum of 15 minutes.
I have been told by another technician that if a battery tester is used, as is allowed by the exceptions under "Batteries -- General Tests" section, that it is not necessary to sound the alarm for 5 minutes/15 minutes as is called for in the Secondary Power Supply section. Can anyone tell me if this is correct? My state is currently under the 2012 edition of the NFPA 72.