I have worked for at least a half dozen engineering firms, and they all did the FA design in this way. We also include a "performance specification" that gives more requirements, and explicitly calls upon the vendor to "provide" (that term meaning "furnish and install") a complete FA system that complies with the applicable codes.
Charlie, Does your performance specification have enough on it to get a permit?
For example in my local jurisdiction, they list to get a permit you need (although they are a little flexible on some detail):
907.1.1 Construction documents.
Construction documents for fire alarm systems shall be submitted for review and approval to the department and the Fire Department prior to system installation. Construction documents shall include, but not be limited to, all of the following:
1.A floor plan that indicates the use of all rooms.
2.Locations of alarm-initiating devices.
3.Locations of alarm notification appliances, including candela ratings for visible alarm notification appliances.
4.Location of fire command center, fire alarm control units, transponders and notification power supplies.
5. Location of remote annunciators.
6. Location of all primary, secondary and local sources of power.
7. Fire alarm riser diagram showing all fire alarm devices indicated on the floor plans. Quantities of devices on the floor plans shall match the quantities indicated on the riser diagram.Riser diagram shall include class and style of circuits and levels of survivability.
The riser diagram shall show the interface of fire safety control functions.
8.Copies of any variances granted by the department or the Fire Department.
9.Legend of all fire alarm symbols and abbreviations used.
10.Design criteria for fire alarm audibility in various occupancies indicated on plans.
11.Fire alarm sequence of operation for the fire alarm system in a matrix format.
12.Classification of the central supervising station