Fire alarm wire is always solid, Why?
I cannot remember why.
Try shoving that into the box when the conductors are #14 and #12 solid.:roll:
I thought stranded wire had to be used.....and not fine stranded (either 12 or 19 strand??) instead of 7 strand.
At least that is how I remember it.
I was watching one our guys do that and we hear a loud 'snap', the terminal strip broke off the PC board. :roll:
Actually it was the other way in the older codes for non-power limited fire alarm wiring. 760-16(c) in the 90 code required that the conductors be solid or bunched tinned with an exception that permitted up to 7 strands for 16 and 18 gauge conductors and up to 19 strands for larger conductors. Not sure when this rule was removed from the code.OOPS... Meant to say I thought FINE stranded wire HAD to be used.
I think it is tradition while the NEC says stranded can be used.
Is that in 760?
............760.49 NPLFA Circuit Conductors.
(C) Conductor Materials. Conductors shall be solid or stranded copper.
760.176 Listing and Marking of NPLFA Cables.
(A) NPLFA Conductor Materials. Conductors shall be 18 AWG or larger solid or stranded copper.
It is not an electrical necessarily. It is requirement in most specifications put out by A&Es. I am noticing that many A&E spec documents are based on older systems and requirements (mainly Simplex). For example I read one last week that called for electro-mechanical horns, stobes with an aluminum plate and white polycarbonate lens and spare bulbs.
For older Fire Alarm Systems, solid conductors were required for survivability before fire rated cables existed.
Today any cable listed as FPLP, FPLR,FPL, FPLP-CI, FPLR-CI, FPL-CL is acceptable for fire alarm system wiring 760.176, 760.179
The old code permitted up to 7 strands for 16 and 18 and up to 19 strands for larger conductors. My understanding of the reason for the rule was that with the higher current loads on the older fire alarm systems, a single strand strand in a 16 gauge with more than 7 strands would be able to carry the supervision current, but may not be able to carry the load of the alarm horns when the system was activated....
For older Fire Alarm Systems, solid conductors were required for survivability before fire rated cables existed.
...