Re: Fire Alarm wiring question.
MAPNET signal is a 34 volt square wave that gets in to everything. Having no support on the FPL cable is sloppy wiring practice,not code compliant, and brings that high level signal close to telco lines, PA system lines, and other systems that can induce hum and noise, and drive people crazy when trying to troubleshoot the problem. We had to eliminate the MAPNET buzz from the audio evacuation portion of a Performing arts center FA system. Our solution included reterminating shields, moving cable runs,though most of the wiring was in EMT, and using an oscilloscope to trace hum and noise voltages.
The shields should be grounded at the origin end to set up a single point grounding arrangement. This makes the shield act like a drain,siphoning off the noise voltage to ground at one point.Multiple grounding points can set up ground currents via resistance between points,and cause interference with low level audio signals. Thios technique is used regularly in pro-audio and broadcasting to reduce noise.
As others have said in this forum, FA wiring is not necessarily respected as it is power limited and low voltage. I have learned a great deal of respect for FA ckts after having to troubleshoot them.
The other problem with circuits like MAPNET is that they contain data,which could be corrupted ,if not carefully routed and terminated. This can cause missed device polling cycles,which show up as missing devices, wrong device, etc.