dnbob
Senior Member
- Location
- Rochester, MN
Curious what people are using for fire alarm wire when ran in conduit. Solid or stranded for the horn/strobe circuits. 24v. DC systems
Curious what people are using for fire alarm wire when ran in conduit. Solid or stranded for the horn/strobe circuits. 24v. DC systems
Here in Rhode Island, we are required to use 14AWG solid in conduit. Blue/white for annunciation, black/red for detection. One fire marshal failed us for using stranded green for grounding conductor, and a different marshal failed us for using wire nuts on the grounds. He made us take them all out and replace them with crimp connectors. Mind you, we had already used those cursed terminal strips on the other joints. Pain in the ass.
Ya, Whats up with those guys! Everything down there is a PITA! Brown & purple for aux power?
Not a problem with the color codes or the termination requirements.
What to do when useing FPL, or MC? Or is that not allowed.
(I'm more involved from the service end,not the install side)
Using both on Long Island, I prefer the stranded myself, Few # 16's and # 14's in 3/4 emt what could be better? The fire alarm cable usually clp3 seems to damage very easily, especially when shielded is required. If I wasn't paying for it I would put everything in pipe and use thhn, as mentioned, being able to use a entire scope of colors makes trouble shooting a lot easier, I'll ask for red\/black, blue/yellow- feed and return for data loop and same for horn strobe and if the system has a speaker circuit i'll use black/white to distinguish it from the data loop.
Rhode Island Boys - What's the argument for solid over stranded in conduit? Any reason behind the code?
I am just curious, i need to run power to the fire alarm sytem, and I was going to do it in 12/2 MC cable. However, coming out of the system itself, i was going to use either 14/2 or 18/2 red wire to the strobes and pullstations, as well as the actual alarms themselves.
Am i on the right track here? Just looking for some input.
Thanks
Here in Rhode Island, we are required to use 14AWG solid in conduit. Blue/white for annunciation, black/red for detection. One fire marshal failed us for using stranded green for grounding conductor, and a different marshal failed us for using wire nuts on the grounds. He made us take them all out and replace them with crimp connectors. Mind you, we had already used those cursed terminal strips on the other joints. Pain in the ass.
..........Generally speaking you can use 18/2 minimum for your initiating loop and 14/2 minimum for your horn strobes. But check the manual first.
as far as i'm concerened in nyc you need to use 3/4" conduit (emt is fine) #12(stranded is fine as well) for 110 vac input & #10 solid green for ground in
"conduit" only no greenfeild
hope it's gonna help you out a little
I can't recall ever using anything smaller and 16 and 12, respectively.
#14 is very common for NAC loops here, but sometimes they are upsized to #12.