Could someone be kind enough to explain the difference between FA Zones and loops?
Also what determines how many zones you need and what determines how many loops you need?
Thank You
A zone is usually a geographic area in a building, a floor or part of a floor, which can be defined by construction (fire rated walls) or purpose (architect defined). A loop is usually the term describing the cable connecting fire alarm initiating or notification devices and the devices themselves. A loop may cross from one zone to another, or you may have more than one loop in a zone, or a combination.
In fire alarm design, the magic numbers for zones are 22,500 sq ft and 300 feet. No zone should be more than 22,500 square feet or longer than 300 feet. These restrictions were much more important before the advent of addressable systems which allow you to pinpoint the exact location of an alarm.
Thank You. What dictates how many loops I need for my FA system? Is this more of a field routing issue as needed for cabling?
The number of loops required is dictated first by the number of devices you have, and second by the number of zones you need. As an example, suppose that the notification appliance circuit (loop) can handle 20 horn/strobes and you need 4 per floor. That would suggest that you could run 5 floors off a single loop. When you go to NFPA 72, you'll find that each floor is considered a separate fire zone, requiring a separate circuit. Conversely, you have a 30 story building and a Siemens XLS addressable fire alarm control unit. Each floor has 8 addressable devices. Since the XLS is capable of handling 252 devices. Since NFPA 72 only requires that the area be identified separately if over 22,500 square feet, and addressable devices can be tagged with their precise location, you could wire the whole building on a single addressable device loop.
As you surmise, there may be matters of convenience that would suggest using more zones than the minimum in order to make the installer's job easier, or facilitate phased construction.
There is a lot of information on zones and zoning in NFPA 72, particularly Annex A. I would suggest getting a copy of the 2013 or 2016 edition and giving it a read.
are there typically two separate loops for the notification devices and the initiation devices or can they both be in one loop?
Yes these are always on different circuits.
Unless...you have Simplex TrueAlert notification appliances. A TrueAlert speaker strobe will have: strobe power, speaker power, and signal loop circuit (SLC). Hat trick!![]()
Oh, now you're just trying to cause trouble!