olly
Senior Member
- Location
- Berthoud, Colorado
- Occupation
- Master Electrician
I see some electricians installing fire foam in every hole and box when they are done with rough in on a residential building. Is that code now?
I see some electricians installing fire foam in every hole and box when they are done with rough in on a residential building. Is that code now?
300.21 Spread of Fire or Products of Combustion
Electrical installations in hollow spaces, vertical shafts, and ventilation or air-handling ducts shall be made so that the possible spread of fire or products of combustion will not be substantially increased. Openings around electrical penetrations into or through fire-resistant-rated walls, partitions, floors, or ceilings shall be firestopped using approved methods to maintain the fire resistance rating.
In many parts of the country the Energy codes require a lot more insulation, including steps to reduce air infiltration at any penetrations in the exterior walls, including interior switch and receptacle boxes in those walls. Possibly some workers find it easier to apply such rules to all boxes instead of trying to figure out which ones actually require it.I'm only required to foam penetrations between floors (including the attic). Horizontal stud penetrations and holes in block for boxes don't require foam (from me. The insulators might do it.)