Around here the electricial inspector doesn't look at anything in the elevator shaft or the elevator equip. room the elevator inspector look at those locations.
Who has final say Fire marshall wants one thing but inspector said he would fail me if I did it??
Around here the electricial inspector doesn't look at anything in the elevator shaft or the elevator equip. room the elevator inspector look at those locations.
Here in Maryland- the State Elevator Inspector has ALL the authority over the Elevator machine room and the Elevator shaft.
We he/she says is what happens,they overide the Fire Marshall and The Electical Inspector.
When I was in the field and did F/A's I had Fire Marshalls that would not even look at those 2 items. The Electrical Inspector would look at the NEC requirements and to see if there were any nEC violations. The Elevator Inspector had the final say.
Heats and smokes in the pit and or shaft depends on if it was sprinklered. If it was The heats and smokes were(are still?) required to be with in 18" of the head. Here was the kicker- In the pit anything below 48" from the pit floor must be watertight. WP boxes,compression fittings,weatherproof lights. If the sprinkler head was 6" off the floor and I was 18" above that I was still inside the 48". There is no such animal as a sealed smoke,so I couldn't put them there regardless.
I would get in touch with the Elevator Inspector for a list of requirements. You may be able to obtain the check list from the elevator installers also
You could ask for the code reference. Usually, when this is done the conflict disappears.
You could ask for the code reference. Usually, when this is done the conflict disappears.