NICK D said:Do You Need Arc Fault Protection For A Jacuzzi Tub 120 Volt And Also Do You Need It For A Window A.C. 240 Volt Both Located In A Bedroom?
(B) Dwelling Unit Bedrooms All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected by a listed arc-fault circuit interrupter, combination type installed to provide protection of the branch circuit.
NICK D said:A Jacuzzi Tub Receptacle Is Not Readily Accessible Does It Still Need Arc Fault?
210.12(B) Dwelling Unit Bedrooms All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected by a listed arc-fault circuit interrupter, combination type installed to provide protection of the branch circuit.
I don't think that arc is sustained enough (or of high enough current) to tick off the arc-fault-sensing portion of the AFCI. It is more likely triggering the GFPE portion of the breaker, IMO.ron said:In order for the igniter to do its job, doesn't it arc? I would think that the AFCI would see the igniter as a arc fault and open as it should.
georgestolz said:If the circuit is supplying wall space receptacles, a 10A breaker is not an option.![]()
georgestolz said:I don't think that arc is sustained enough (or of high enough current) to tick off the arc-fault-sensing portion of the AFCI. It is more likely triggering the GFPE portion of the breaker, IMO.
sparky_magoo said:Can anyone explain to me why a fire place ignitor reqiures AFCI protection?
The obvious answer is for me to put the fire place ignitor on another ckt. The inspector won't buy off on this. The house is already rocked. The inspecptor sez I must make the ignitor work on the AFCI ckt. My boss sez I must finish by Monday. I have other issues I must finish Monday. This is a custom house with many change orders.
I have all change orders under control except for the fire place ignitor.
What is a poor electrician to do?