The following was a proposal for the 2011 code. Note that feeders begin at the load side of the service overcurrent protective device.This scenario is really really odd because 240.21 and 430.28 all are about feeder taps, but we are not tapping at any feeders. We are tapping lugs on the load side of a service fuse. So tap rule does this apply to?
In the 2020 the code language was changed to try and clarify the issue with the underlined text below being added to 240.21(B), but I think the rejected language in my proposal above was better10-45 Log #4825 NEC-P10 Final Action: Reject
(240.21(B))
_______________________________________________________________
Submitter: Don Ganiere, Ottawa, IL
Recommendation: Add text to read as follows:
(B) Feeder Taps. Conductors shall be permitted to be tapped, without
overcurrent protection at the tap, to a feeder as specified in 240.21(B)(1)
through (B)(5). Feeder taps shall be permitted to originate at the load terminal
of an overcurrent protective device. The provisions of 240.4(B) shall not be
permitted for tap conductors.
Substantiation: This type of installation is permitted in many areas, but the
code does not specifically permit it. The additional wording will make it clear
that this is a code compliant installation. As long as all of the conditions of this
section are complied with the point of origination of the tap conductor does not
create any additional hazard.
Panel Meeting Action: Reject
Panel Statement: The proposed language is not necessary as the present
language permits such installation where appropriate.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
(B) Feeder Taps.
Conductors shall be permitted to be tapped, without overcurrent protection at the tap, to a feeder as specified in 240.21(B)(1) through (B)(5). The tap shall be permitted at any point on the load side of the feeder overcurrent protective device. Section 240.4(B) shall not be permitted for tap conductors.