packersparky
Senior Member
- Location
- Wisconsin
- Occupation
- Inspector
Ok but by your account any service conductors not just fire pump would have to comply 230.6. So if you have any service conductors inside room that go to trough with miltiple service disconnect then by your account need to be in brick or concrete encased. How many times you have seen that in electric room?
Sent from my SM-G935U using Tapatalk
I am not talking about service conductors that do not supply a fire pump. The rules in Article 230 deal with those.
695.6(A)(1) is for service conductors that supply a fire pump.