Three phaseThis a 3 phase non-SDS, single phase SDS, or something else?
So it is OK to pull neutral to the fire pump controller from generator without having objective current?So long as the generator neutral isn't bonded to ground as well, there will be no objectionable current.
No, I didn't realize they go to the same lug in the controller. No, that isn't right. Why is it like that?So it is OK to pull neutral to the fire pump controller from generator without having objective current?
The controller is probably (usually) service rated.No, I didn't realize they go to the same lug in the controller. No, that isn't right. Why is it like that?
I'd bet the next mortgage payment you're correct.The controller is probably (usually) service rated.
I've never seen one. Is there no way to unbond the neutral or to add a ground out?The controller is probably (usually) service rated.
Usually a separate service or an isolated service is required to them. The pump itself does not use a neutral, but has to be brought to all service disconnects if present. They are thousands out there like that with no issues.I've never seen one. Is there no way to unbond the neutral or to add a ground out?
There should be no bonding of the neutral at the gen.No, I didn't realize they go to the same lug in the controller. No, that isn't right. Why is it like that?
So it is OK to pull neutral to the fire pump controller from generator without having objective current?
But the diagram shows the no bond in the generator so the op is right.So long as the generator neutral isn't bonded to ground as well, there will be no objectionable current.
The OP shows the bond in the main panel and a solid neutral transfer switch. And then the neutral bonded to ground again at the pump controllerBut the diagram shows the no bond in the generator so the op is right.
Anytime you have more than one service disconnect enclosure and you use the individual grounding electrode allowance from each of the service disconnects you will have a bond at the electrode that ties the neutral path togetherThe OP shows the bond in the main panel and a solid neutral transfer switch. And then the neutral bonded to ground again at the pump controller
generator and FPL utility service@loco79
You have to supply more information to get the answer you are looking for. What powers the fire pump? Just the generator?? Does the generator supply only the fire pump or does it also serve other loads?