I have multi campus style building where customer owned transformer primary delta 13.2k to secondary wye 277/480V is feeding the fire pump controller/ats/breaker and jockey pump controller. The fire pump and jockey pump are both 480V three phase load
Engineer wants to bring neutral from the secondary side of the customer owned transformer to the fire pump controller/ats/breaker all in one but tells me their is no neutral lug in fire pump controller/ats/breaker all in one. He says there is only ground lug in fire pump controller/ats/breaker all in one.
Can he bring the neutral from secondary of customer owned transformer and land in ground lug since there is no neutral lug in fire pump controller/ats/breaker all in one or not?
Engineer wants to bring neutral from the secondary side of the customer owned transformer to the fire pump controller/ats/breaker all in one but tells me their is no neutral lug in fire pump controller/ats/breaker all in one. He says there is only ground lug in fire pump controller/ats/breaker all in one.