olly
Senior Member
- Location
- Berthoud, Colorado
- Occupation
- Master Electrician
It has to be sized to handle the locked rotor current for the jockey and fire pumps, plus and auxiliary loads like the controllers. That looks like just under or at 400 amps, not 1,000 amps.I am reviewing a one-line diagram that had a CT / Disconnect that was 200A and now its 1000A and the pump size never changed. The Electrical engineer claims that it needs to be 5x larger due to fire code. Is he correct that this disconnect needs to be 5x larger?
View attachment 2554557
I didn't check the math but that looks about right as that is on the 208 side and it needs to carry locked rotor on the 480 side motor. Note that that transformer will need to be 208 delta X 480Y.I am reviewing a one-line diagram that had a CT / Disconnect that was 200A and now its 1000A and the pump size never changed. The Electrical engineer claims that it needs to be 5x larger due to fire code. Is he correct that this disconnect needs to be 5x larger?
View attachment 2554557
I didn't pay attention to that. My bad.I didn't check the math but that looks about right as that is on the 208 side and it needs to carry locked rotor on the 480 side motor. Note that that transformer will need to be 208 delta X 480Y.
At first glance I did too.I didn't pay attention to that. My bad.
However, if you apply table 9.5.1.1(a) from NFPA 20, you'll see that the locked rotor current for the fire pump should be 277 at 480v, not 380. The jockey pump goes up to 19.2 amps.I didn't pay attention to that. My bad.
In addition, if you use 208 motors you could also get rid of the 1000 amp disco. as the fire pump controller and the jocky pump controller can/will be service rated and make this much simpler, cheaper and reliable.I would question why he doesn't spec a 208 fire pump and make it less complicated. 40 HP is not unreasonable to run on 208.
The big problem is that the POCO bills capacity fee's based off of the first disconnect from the transformer. So If he would have went with a 208 pump the disconnect could have been smaller?In addition, if you use 208 motors you could also get rid of the 1000 amp disco. as the fire pump controller and the jocky pump controller can/will be service rated and make this much simpler, cheaper and reliable.
Does that mean the disconnect off the POCO transform could be smaller? 1000A is still not making sense to meHowever, if you apply table 9.5.1.1(a) from NFPA 20, you'll see that the locked rotor current for the fire pump should be 277 at 480v, not 380. The jockey pump goes up to 19.2 amps.
the 208 transformer is a YI didn't check the math but that looks about right as that is on the 208 side and it needs to carry locked rotor on the 480 side motor. Note that that transformer will need to be 208 delta X 480Y.
No, I'm saying you don't need the disconnect at all. The fire pump controller is rated as service equipment and you run service conductors directly to it from the CT can. The path must be "outside the building" (usually underground to the fire pump room). As for POCO charges you need to have a chat with a capable service planner and explain that this is a fire pump.The big problem is that the POCO bills capacity fee's based off of the first disconnect from the transformer. So If he would have went with a 208 pump the disconnect could have been smaller?
I was referring to the step-up transformer shown on the load side of the disconnect. You are stepping up from 208 to 480 so it needs to be a 208 delta X 480Y.the 208 transformer is a Y
That 600% is for the fire pump controller, "an assembly listed for fire pump service". This is for the case where you have a tap ahead of the meter or service entrance panelboard and the only disconnecting means for the fire pump is the fire pump controller.I am actually in the middle of designing a service for a 40Hp fire pump. I have an 800A fused disconnect because according to NEC the overcurrent is required to handle 600% of the FLA for at least 2 minutes.
My service is also 240 3phase delta... so my numbers will be a little lower, so by the numbers he is looking at 930A so he would need the 1000A
My question for you is why do you have disconnect ahead of the fire pump controller?I am actually in the middle of designing a service for a 40Hp fire pump. I have an 800A fused disconnect because according to NEC the overcurrent is required to handle 600% of the FLA for at least 2 minutes.
My service is also 240 3phase delta... so my numbers will be a little lower, so by the numbers he is looking at 930A so he would need the 1000A
Because Code says I can. 695.4 "General. A single disconnecting means and associated overcurrent protective device shall be permitted to be installed between the fire pump source power source (in my case the utility) and one of the following.... 1. a listed fire pump controller." I have a very long run and felt it better to have the disconnect.My question for you is why do you have disconnect ahead of the fire pump controller?
Well, of course you can but all it does is add a lot of cost and reduce reliability.Because Code says I can. 695.4 "General. A single disconnecting means and associated overcurrent protective device shall be permitted to be installed between the fire pump source power source (in my case the utility) and one of the following.... 1. a listed fire pump controller." I have a very long run and felt it better to have the disconnect.
Not to argue you with you but that is not how the code words it. Also, by not including the full statement you are taking the code out context. But if I am wrong, please explain.That 600% is for the fire pump controller, "an assembly listed for fire pump service". This is for the case where you have a tap ahead of the meter or service entrance panelboard and the only disconnecting means for the fire pump is the fire pump controller.