fire pump electrical connection

Status
Not open for further replies.

New EE

Member
Location
California
I'm working on a fire pump replacement project and can't seem to grasp what I'm doing wrong. The electrical permit reviewer
commented on the drawings saying that "Verify the Circuit breaker on the emergency power side complies with NEC 695.4(A).
I spoke to him and he had mentioned that I need to tap the line side with a seperate breaker. Please refere to attached one
line diagram.

Also he made another comment "Verify the circuit breaker size on the emergency power side complies with NEC 695.4(B).
He said that he thought my 3P100A was too large and should be sized on the motor rating. I believe i just need to change
it from 3P100A to 3P70A. Is that correct?
 

Attachments

  • one line.pdf
    65.8 KB · Views: 3
I'm working on a fire pump replacement project and can't seem to grasp what I'm doing wrong. The electrical permit reviewer
commented on the drawings saying that "Verify the Circuit breaker on the emergency power side complies with NEC 695.4(A).
I spoke to him and he had mentioned that I need to tap the line side with a seperate breaker. Please refere to attached one
line diagram.



Also he made another comment "Verify the circuit breaker size on the emergency power side complies with NEC 695.4(B).
He said that he thought my 3P100A was too large and should be sized on the motor rating. I believe i just need to change
it from 3P100A to 3P70A. Is that correct?

You need to comply with A OR B but I think you have a problem meeting B with that 3000 amp breaker on the emerg bus ahead of the fire pump breaker.

Have to check on the 70 vs 100 as I don't know off the top of my head.
 