Please see attached sketch shows service conductor tapped separate enclosure in switchboard ahead of main service disconnects.
The service conductors feed 400A main service fused disco fused at 400A.
Feeder labeled FDR#1 in sketch has 3#2+1#6G load side of the 400A service fused disco that feeds fire pump controller.
Feeder labeled FDR#2 supply from Fire pump Controller to Fire Pump is 3#2+1#6G.
Fire pump is 208V 3 phase, 20HP, Locked Rotor current of 360A
NEC 2017 section 695.6(B)(2) says conductor size ampacity minimum for motor only comply with 430.22 and voltage drop. Note it does Not say those conductors are phase conductors or equipment grounding conductor
There fore it is not clear how to size Equipment grounding conductor
Questions:
1 In attached sketch what code section one can use to size FDR #1 and FDR #2 equipment grounding conductor for Fire Pump?
2. #6 equipment grounding conductor (EGC )ok or its undersized?
The service conductors feed 400A main service fused disco fused at 400A.
Feeder labeled FDR#1 in sketch has 3#2+1#6G load side of the 400A service fused disco that feeds fire pump controller.
Feeder labeled FDR#2 supply from Fire pump Controller to Fire Pump is 3#2+1#6G.
Fire pump is 208V 3 phase, 20HP, Locked Rotor current of 360A
NEC 2017 section 695.6(B)(2) says conductor size ampacity minimum for motor only comply with 430.22 and voltage drop. Note it does Not say those conductors are phase conductors or equipment grounding conductor
There fore it is not clear how to size Equipment grounding conductor
Questions:
1 In attached sketch what code section one can use to size FDR #1 and FDR #2 equipment grounding conductor for Fire Pump?
2. #6 equipment grounding conductor (EGC )ok or its undersized?