Fire pump Equipment Grounding Conductor

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Please see attached sketch shows service conductor tapped separate enclosure in switchboard ahead of main service disconnects.

The service conductors feed 400A main service fused disco fused at 400A.

Feeder labeled FDR#1 in sketch has 3#2+1#6G load side of the 400A service fused disco that feeds fire pump controller.

Feeder labeled FDR#2 supply from Fire pump Controller to Fire Pump is 3#2+1#6G.

Fire pump is 208V 3 phase, 20HP, Locked Rotor current of 360A

NEC 2017 section 695.6(B)(2) says conductor size ampacity minimum for motor only comply with 430.22 and voltage drop. Note it does Not say those conductors are phase conductors or equipment grounding conductor
There fore it is not clear how to size Equipment grounding conductor

Questions:

1 In attached sketch what code section one can use to size FDR #1 and FDR #2 equipment grounding conductor for Fire Pump?

2. #6 equipment grounding conductor (EGC )ok or its undersized?


392ffc958b1a910c7142a9cc6bc23ac4.jpg
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Since there is nothing in Article 695, to address the EGC, then the rules in Article 250 apply. See 90.3
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Since there is nothing in Article 695, to address the EGC, then the rules in Article 250 apply. See 90.3

Ok it gets confusing when voltage drop is involved. If phase conductors are increased then so are EGC but what is the intended EGC? What is the intended EGC to work 250.122(b)?

Is the intended EGC based on 400A fuse for Fdr#1 and intended EGC based on overcurrent protection in FP controller for FDR #2 Or some other way?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Is the intended EGC based on 400A fuse for Fdr#1 and intended EGC based on overcurrent protection in FP controller for FDR #2 Or some other way?
Yes, so #6 is too small for feeder #1.
The whole scenario is likely to change when you look at voltage drop.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Most likely.. but you need the controller OCP to make sure.
To CYA you can always size it the same as the phase conductors....can't go wrong then :)
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
So still sized based on the upstream 400 amp device.

But if someone places the dial of the motor controller factory installed internal breaker to 1200A (20x full load amps) then sizing based on 400A would be not correct.

Do fire pump motor controller internal breakers have dial or is it factory set so no one can tamper with it? If factory set then what is it the setting set at 6x fla or 20x fla?
 