Fire pump Equipment Grounding Conductor

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
But if someone places the dial of the motor controller factory installed internal breaker to 1200A (20x full load amps) then sizing based on 400A would be not correct.

Do fire pump motor controller internal breakers have dial or is it factory set so no one can tamper with it? If factory set then what is it the setting set at 6x fla or 20x fla?
No matter what the downstream instantaneous setting is, you can't flow more current than the upstream 400 amp device will permit.
In addition, if that is the only dial, the device is an instantaneous trip device and 250.122(D)(2) would apply.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
No matter what the downstream instantaneous setting is, you can't flow more current than the upstream 400 amp device will permit.
In addition, if that is the only dial, the device is an instantaneous trip device and 250.122(D)(2) would apply.

Would not the fire pump controller isolate the upstream breaker so that current flow on line side is Not the same on load side?
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Is it possible or not is my concern? I just dont know


Series fault impedance, no auto transformer involved so what the controllers sees the 400 amp fuses will so.

If you give me the run lengths from the MDP to the fire pump and the kva of the POCO transformer I can run some rough numbers for you.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Series fault impedance, no auto transformer involved so what the controllers sees the 400 amp fuses will so.

If you give me the run lengths from the MDP to the fire pump and the kva of the POCO transformer I can run some rough numbers for you.
So I suggest you take mbrooke up on the offer.

Roger
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Would not the fire pump controller isolate the upstream breaker so that current flow on line side is Not the same on load side?
There is nothing in the controller that creates energy or power, so how could there be more energy or power on the load side of the controller than on the line side?
 