No matter what the downstream instantaneous setting is, you can't flow more current than the upstream 400 amp device will permit.But if someone places the dial of the motor controller factory installed internal breaker to 1200A (20x full load amps) then sizing based on 400A would be not correct.
Do fire pump motor controller internal breakers have dial or is it factory set so no one can tamper with it? If factory set then what is it the setting set at 6x fla or 20x fla?
In addition, if that is the only dial, the device is an instantaneous trip device and 250.122(D)(2) would apply.