There is the main switchboard located in a parking garage area. It meets all code required space and protection requirements. The building has a fire pump controller (main and generator backup) located in a separate room approximately 100 feet away. The question is about feeder conductors (tap ahead of main with disconnect) from the main switchboard to the fire pump controller. (2014) Section 695.6, Exception to (A)(2)(d). It mentions "electrical equipment room". Are they implying that I need such a room? Or, is providing a 2-hour rated feeder from the switchboard, to the disconnect, to the fire pump controller sufficient? I read it such that if you have an electrical room, the 2-hour rating is not required inside the room. Am I missing something?