Fire pump generator conductor connected without overcurrent protection

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
See attached sketch. I. have onsite generator which feeds fire pump. However the conductor from generator to enclosed circuit breaker 200A have no overcurrent protection and they run several hundred feet. When they enter the building a 200A enclosed circuit breaker is provided.

Should not the conductors require overcurrent protection?

IMG_6867.jpg
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Because it is broken up into two circuits, each with their only OCPD at the load end.
Also, I am not sure that you can have that 200 amp OCPD on the line side of the transfer switch.

I dont follow. How is this feeder? Its connected on line side of 100a breaker.