Fire Pump Grounding

Status
Not open for further replies.

dschomer

Member
We have opted to serve a fire pump from a separate utility service derived from the same utility transformer serving the main building service. We have bonded all of the available grounding electrodes at one point and then to the service neutral. We then showed the neutral of the fire pump tied to the same ground box. The AHJ wants a separate G.E.S. for the fire pump. Is this actually compliant?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
My thoughts would be "no". One structure would require all grounding electrodes to be connected (250.50)
 