I searched the forum earlier today for this but couldn't find anything.
We designed a life safety upgrade project for a 14 story apt. building that including adding sprinklers with a fire pump, adding a new fire alarm system and adding a new diesel generator. The project was designed two years ago and currently under construction.
Since the building is a high rise (over 75'), we provided emergency power for the fire pump as well as a separate utility service (both at 208V 3 phase).
- the fire pump is 75HP 208V and is manufactured by Patterson
- the fire pump controller / automatic transfer switch is manufactured by Joslyn Clark and is Wye-Delta closed (not across the line)
- the jockey pump is 1 1/2HP 208V and is manufactured by Patterson
- the jockey pump controller is manufactured by Joslyn Clark
I originally had the tap for the jockey pump after the fire pump controller and before the fire pump in a separate enclosure. Since the motor has 12 leads with 6 that get paired (for wye delta starting), I can't make the tap here now. So now I need to make the tap ahead of the fire pump controller/automatic transfer switch.
So this leads to my two questions:
- is emergency power required for the jockey pump? I have researched IBC 2006, NEC 695 and NFPA 20 and do not believe it is.
- what is the best way to make the tap ahead of the fire pump controller if it is being fed with parallel sets from the new utility service?
Thanks,
Tom
We designed a life safety upgrade project for a 14 story apt. building that including adding sprinklers with a fire pump, adding a new fire alarm system and adding a new diesel generator. The project was designed two years ago and currently under construction.
Since the building is a high rise (over 75'), we provided emergency power for the fire pump as well as a separate utility service (both at 208V 3 phase).
- the fire pump is 75HP 208V and is manufactured by Patterson
- the fire pump controller / automatic transfer switch is manufactured by Joslyn Clark and is Wye-Delta closed (not across the line)
- the jockey pump is 1 1/2HP 208V and is manufactured by Patterson
- the jockey pump controller is manufactured by Joslyn Clark
I originally had the tap for the jockey pump after the fire pump controller and before the fire pump in a separate enclosure. Since the motor has 12 leads with 6 that get paired (for wye delta starting), I can't make the tap here now. So now I need to make the tap ahead of the fire pump controller/automatic transfer switch.
So this leads to my two questions:
- is emergency power required for the jockey pump? I have researched IBC 2006, NEC 695 and NFPA 20 and do not believe it is.
- what is the best way to make the tap ahead of the fire pump controller if it is being fed with parallel sets from the new utility service?
Thanks,
Tom