Fire Pump Listing

Status
Not open for further replies.

johnnym

Member
Location
Vermont
I recently saw a newly installed residential sprinkler system with a Gould Irri-gator used for a pump. 695.10 NEC requires all electric motors to be listed for fire pump service. I don't believe an irrigation pump is listed for this purpose. Are there exceptions in another code that would allow this? i.e NFPA 13D or NFPA 20. Am I missing something?
 
Pierre C Belarge said:
Article 695 does not apply to the installation you are referring to.

Pierre that seems to make sense and I do not doubt you but can you point to something that tells us that?

I looked at the scope and it did not help. :confused:
 
I just checked the NEC handbook and the commentary after 695.1 says that article 695 does not apply to one and two family dwellinds. NFPA 13 D covers that. You are right on Pierre.

Thanks
 