Fitzdrew516
 - Cincinnati, OH
I have recently designed an industrial building with a service size of 2000A with a 100% rated MCB (480V). My total calculated loads are about 1200 amps and all of the equipment is subject to change (one of the reasons I decently oversized the service). Soon after this phase is completed an office will be added on so I was banking on 100-200 amps of power for the future office build out.
Well we have recently been told that we will need a fire pump for the building now and since electric is the cheapest option, I assume it will be an electric fire pump. My question is this - Do I have to account for the load of the fire pump in my calculations for the main service? The fire pump will be tapped ahead of the main and utilize it's own section of switchgear. I would think the load would have to be accounted for, but since the fire pump never runs (unless a fire obviously) it seems like there may be some sort of exception out there somewhere.
As you may be able to guess my concerns are with the client possibly significantly adding/changing the equipment that is scheduled + future office load + fire pump load could get close to that 2,000 number. And yes my calculations are based on "calculated load" and my main is 100% rated so technically my calculated load could be over 2,000A, but sometimes it's hard to get that concept through a plans reviewer's head. For example - They often would just see 2,200A at the bottom of the panel schedule on a 2,000A service and freak out without understanding the demand factors, etc. I'm just trying to make this process as smooth as possible.
Thanks,
-Drew
Thanks,
-Drew