Fire Pump - Reliable source

Status
Not open for further replies.

WORF582

Member
We are wiring a fire pump at a Hospice. The building has a generator that backs up the entire service. We installed a seperate service from the utility to the pump controller. I am considering the utility company as a reliable source of power and have made no provitions for back up power to the pump. The pump installer has not installed a fire pump ATS.

Am I correct in considering the utility as being the reliable source of power?

thanks
 

dkidd

Senior Member
Location
here
Occupation
PE
Reliable is in the judgment of the AHJ. Guidance is given in NFPA 20 Annex A A.9.3.2.
 

RICK NAPIER

Senior Member
Location
New Jersey
I had this issue in NJ and was informed that the utlities have thier own requirements to meet for a reliable source and that all the electric utilitiees in NJ qualified. The utility also said it was very difficult to find an electric utility that didn't qualify.
 