I don't believe the NEC says anything about the rating of fire pump rooms.
NFPA 20, on the other hand, seems to require a 2 hour separation in all high-rise buildings, and either a 2 hour or 1 hour separation in other buildings - the 1 hour rating is allowed if both the pump room and building are fully sprinklered.