The OP has not been back since Tuesday so maybe he got his answer.
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 14, 2022 #21 The OP has not been back since Tuesday so maybe he got his answer.
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Apr 14, 2022 #22 hhsting said: Difference is in listed equipment changing lug may invalidate the listing. Its like changing what manufacturer provided Click to expand... That is not true according to UL, which says it is up to the AHJ to approve or reject field modifications.
hhsting said: Difference is in listed equipment changing lug may invalidate the listing. Its like changing what manufacturer provided Click to expand... That is not true according to UL, which says it is up to the AHJ to approve or reject field modifications.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Apr 14, 2022 #23 Or he didn't like seeing his post hijacked. 5 questions on the size of an EGC lug that didn't get answered in another post.