jahilliard
Senior Member
We need to provide service to 2 new Fire Pumps for an existing Wal-Mart. The 480V transformer is directly adjacent to the building and the Sprinkler Room is approx 80' away on the other side of the exterior wall. Is it NEC compliant to run conduit and conductors underground from the transformer to the exterior wall, travel along the outside of the building along the exterior wall and punch through the wall directly into the sprinkler room? The main question would that be considered "outside the building" therefore not requiring the Fire rating, Concrete encasement etc.? This is completely separate from any other services currently coming to the building and will not have any means of disconnect ahead of the Pump Controllers. The plan detail describes the installation in this way but I am not sure the conduit traveling along the exterior of the wall is considered "outside the building".