A new dedicated service for a 125 HP Fire Pump at 480(460)V requires what ampacity Transocket?
The controller, supplied with the Fire Pump, is service entrance rated and includes a properly sized, Locked Rotor, overcurrent device. Conductors work out to be 3/0 and the overcurrent device works out to be 1000 amp.
I don't think the transocket is technically a disconnect, however, removing the meter will result in the Fire Pump being de-energized.
Is the transocket required to be 1000 amp rated?
Why couldn't the transcocket be 400 amp rated?
The controller, supplied with the Fire Pump, is service entrance rated and includes a properly sized, Locked Rotor, overcurrent device. Conductors work out to be 3/0 and the overcurrent device works out to be 1000 amp.
I don't think the transocket is technically a disconnect, however, removing the meter will result in the Fire Pump being de-energized.
Is the transocket required to be 1000 amp rated?
Why couldn't the transcocket be 400 amp rated?