gadfly56
Senior Member
- Location
- New Jersey
- Occupation
- Professional Engineer, Fire & Life Safety
I'm paraphrasing here, but the first sentence basically says "Where the service voltage is different than the fire pump voltage a transformer shall be permitted between the system supply and the fire pump controller."
So this only applies when the source voltage is different than the fire pump voltage. Note that "source" or "service" refers back to the sources listed in 695.3, so the source or service is the "Electric Utility Service Connection". As a result, 695.5 only applies for a customer owned transformer after the service, or a transformer connected to a generator or an on site power production facility.
Again, I still agree with you that the utility primary fusing should carry the locked rotor current, or an alternate source must be provided, but that's just not the right paragraph to quote.
I do not agree with this:
And overcurrent protection is permitted on the secondary side of a utility transformer that supplies a fire pump, just not on the secondary of a privately owned transformer.
There is no customer owned transformer. There is ONLY the POCO transformer. Now what????