I am looking for some input concerning Fire Pump connections. My head starts swimming every time I look at article 695. If there is a separate utility service feeding the fire pump, and the fire pump controller handles the locked rotor protection required, and the feeder conductors are sized at 125% of the FLC of all the motors, can't the service disconnect just be a non fused disconnect sized for the FLC without having to provide overcurrent protection sized at the locked rotor amps?