I have a project to wire a simple bathroom exhaust fan in a commercial building that is being vented directly outside the building. The sheet metal contractor is telling me it needs a fire/smoke damper but I'm pretty sure if it is being directly exhausted outside the building whats the point of keeping the smoke inside. Any help would be appreciated.
Not sure if it applies but here is some info from IBC to consider:
717.5.4 Fire partitions. Ducts and air transfer openings
that penetrate fire partitions shall be protected with listed
fire dampers installed in accordance with their listing.
140
Exceptions: In occupancies other than Group H, fire
dampers are not required where any of the following
apply:
1,2,3,
4. Such walls are penetrated by ducted HV AC systems,
have a required fire-resistance rating of 1
hour or less, and are in buildings equipped
throughout with an automatic sprinkler system in
accordance with Section 903.3.1.1 or 903.3.1.2.
For the purposes of this exception, a ducted
HV AC system shall be a duct system for conveying
supply, return or exhaust air as part of the
structure's HV AC system. Such a duct system
shall be constructed of sheet steel not less than
No. 26 gage thickness and shall be continuous
from the air-handling appliance or equipment to
the air outlet and inlet terminals.