before we get into the weeds
It went from a small exhaust fan to kitchen fire suppression. Too late.
before we get into the weeds
It went from a small exhaust fan to kitchen fire suppression. Too late.
Raider,
The answer is no, the venting goes directly from the bathroom to an adjacent exterior wall.
Is the bathfan itself located in the ceiling?
The only reason that I ask is this is an issue with apartment complexes where the ceiling is fire rated to protect the apartment above. If the fan is located in the rated ceiling there is a penetration of the ceiling membrane that must be protected.
What I have seen done to fix this is the fan being located in a dropped ceiling below that actual rated ceiling.
Chris
The ceiling can (might) still be rated even if it's attic space above in which case a damper is still required.
OP needs to find out if it's a rated ceiling, and if so, what that rating is (in hours).
Might be a side yard issue.
Putting the fan in the dropped ceiling area only helps if the duct then goes out the wall(s) or up a fire rated chase and not up to the roof through the fire barrier.Is the bathfan itself located in the ceiling?
The only reason that I ask is this is an issue with apartment complexes where the ceiling is fire rated to protect the apartment above. If the fan is located in the rated ceiling there is a penetration of the ceiling membrane that must be protected.
What I have seen done to fix this is the fan being located in a dropped ceiling below that actual rated ceiling.
Chris
Putting the fan in the dropped ceiling area only helps if the duct then goes out the wall(s) or up a fire rated chase and not up to the roof through the fire barrier.
Yup. A fan in the structural ceiling could not, by definition, exit directly to the wall. This situation came up in the first place in regard to going through the unit above to the roof.Please see post #23 for the answer to that question.
That's only in residential, you have different restrictions in commercial which is where this is located, but he also did not give us all of the particulars.Only if it's less than 5 feet to the adjacent building.
Yup. A fan in the structural ceiling could not, by definition, exit directly to the wall. This situation came up in the first place in regard to going through the unit above to the roof.
That's only in residential, you have different restrictions in commercial which is where this is located, but he also did not give us all of the particulars.
Right and depending on the occupancy you may well be required to have 60' side yards for a commercial building.No. The IBC is for commercial as well. The IRC is for residential only.
Right and depending on the occupancy you may well be required to have 60' side yards for a commercial building.
Sure, but that's a matter for the zoning ordinance. As far as the IBC is concerned you can have unlimited unprotected openings if your separation is 30 feet or greater.