bphgravity
Senior Member
- Location
- Florida
I need some assistance on requirements for cables and conduits penetrating rated walls.
The first question concerns boxes installed in rated walls. I have a contractor that has installed a couple "cut-in" boxes in a 1hr wall for a commercial remodel. According to the section concerning this issue in Volume One of the UL Fire Resistance Directory, "The metallic outlet or switch boxes shall be securely fastened to the studs..."
Based on this, wouldn't this prohibit the use of cut-in boxes? The problem is that there is nothing in both the FBC and the NEC that makes this specification. What enforcement authority do I have referencing a UL spec?
The second issue is concerning the penetrations. The contractor used type MC Cable tested for fire wall penetration. However, the plans did not provide what UL system number the installation is complying with. The contractor used a hammer to bust out a hole approximately 2 in round a passed the cable through at an angle almost parallel to the wall. They then filled the whole with fire caulk. It is my understanding that when penetrating a fire wall with any cable or conduit, it must be at a nearly perpendicular (90?) angle to the wall and the annular space around the opening is limited based on the wiring method type. The contractor is stating that the cable does not pass through the fire wall, but through one side and stays in the wall cavity to a box in the tenant space. They do not feel the penetration must meet a UL system spec.
Any help?
The first question concerns boxes installed in rated walls. I have a contractor that has installed a couple "cut-in" boxes in a 1hr wall for a commercial remodel. According to the section concerning this issue in Volume One of the UL Fire Resistance Directory, "The metallic outlet or switch boxes shall be securely fastened to the studs..."
Based on this, wouldn't this prohibit the use of cut-in boxes? The problem is that there is nothing in both the FBC and the NEC that makes this specification. What enforcement authority do I have referencing a UL spec?
The second issue is concerning the penetrations. The contractor used type MC Cable tested for fire wall penetration. However, the plans did not provide what UL system number the installation is complying with. The contractor used a hammer to bust out a hole approximately 2 in round a passed the cable through at an angle almost parallel to the wall. They then filled the whole with fire caulk. It is my understanding that when penetrating a fire wall with any cable or conduit, it must be at a nearly perpendicular (90?) angle to the wall and the annular space around the opening is limited based on the wiring method type. The contractor is stating that the cable does not pass through the fire wall, but through one side and stays in the wall cavity to a box in the tenant space. They do not feel the penetration must meet a UL system spec.
Any help?