LAGuy

New member
Location
Los Angeles
Hi, I have a below grade garage with living space above. Both garage and residence have fire sprinklers installed. Do I still need to fire box the recessed lights? My plans state that if both garage and residence have sprinklers (CRC R302.5.1), I do not need a fire door. My thinking is then why would I need fire boxes for the recessed lights?

Any info is appreciated, especially code that I can reference. Thanks!
 
I am closing this thread, in accordance with the Forum Rules.

This site is designed for:

  • Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals


* This NEC Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.
If you feel this action to be in error, feel free to contact me via PM to explain.

A reminder to all members, if you see a questionable post, feel free to report it by clicking the
report-40b.png
button at the bottom left corner of the post.
 
The door still needs to be self closing and self latching and gasketed, so you may as well put in a rated door. Per R302.4.1.1 you still need to protect all other opening per their listing, so yes you would need to install boxes. You also still need 5/8 drywall on the lid.
 