first disc for service

Status
Not open for further replies.

shelco

Senior Member
I should know this but my code book has come up missing and I am having trouble remembering(age).

Replaceing service and fused panel with load center. Need disconnecting means outside next to the meter base then to the load center. Is the load center now a sub panel or can I run seu to the new load center from disc as long as I don't bond the Neut in the disc.? LC is in middle of home.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: first disc for service

The panel is now a subpanel and requires 4 conductors which would be SER cable. Neutral bonding and grounding electrode conductors must terminate in the disconnect and grounding and grounded conductors must be separate in the subpanel.
 

shelco

Senior Member
Re: first disc for service

Thanks
I thought that hat was the case but just couldn't get the brain to jump start.
 