dec_primary
Member
- Location
- New York
- Occupation
- Electrical Engineer
Hi All,
I'm working with a 480/277V 2000A switchgear which has no labels on the cover or the breakers on the AIC rating. I'm adding a stepdown 112.5kVA transformer and a 400A panel downstream for EV chargers. The building department wants me to show the available fault current and the short circuit rating at each piece of equipment.
Please bear with me as this is a first for me
1) If I cannot find the AIC rating, does this mean I have to do a full short circuit study, going all the way upstream and contacting the utility to find out what their transformer's AFC/impedances are?
2) If I did have the AIC rating, would all I need to show to the building department be the available fault current at the secondary of my new transformer and panel, and the appropriate breaker SSCR ratings to show I'm covering the maximum available fault current?
I'm working with a 480/277V 2000A switchgear which has no labels on the cover or the breakers on the AIC rating. I'm adding a stepdown 112.5kVA transformer and a 400A panel downstream for EV chargers. The building department wants me to show the available fault current and the short circuit rating at each piece of equipment.
Please bear with me as this is a first for me
1) If I cannot find the AIC rating, does this mean I have to do a full short circuit study, going all the way upstream and contacting the utility to find out what their transformer's AFC/impedances are?
2) If I did have the AIC rating, would all I need to show to the building department be the available fault current at the secondary of my new transformer and panel, and the appropriate breaker SSCR ratings to show I'm covering the maximum available fault current?