I'm working with a 480/277V 2000A switchgear which has no labels on the cover or the breakers on the AIC rating. I'm adding a stepdown 112.5kVA transformer and a 400A panel downstream for EV chargers. The building department wants me to show the available fault current and the short circuit rating at each piece of equipment.
Please bear with me as this is a first for me
1) If I cannot find the AIC rating, does this mean I have to do a full short circuit study, going all the way upstream and contacting the utility to find out what their transformer's AFC/impedances are?
2) If I did have the AIC rating, would all I need to show to the building department be the available fault current at the secondary of my new transformer and panel, and the appropriate breaker SSCR ratings to show I'm covering the maximum available fault current?
jim dungar
Wisconsin
PE (Retired) - Power Systems
You need to prove any additions made to the 480V existing equipment have the appropriate AIC, so you need to know the available fault current or a worst case.
If all you need is to determine a minimum AIC/SCCR for devices and equipment after the transformer, you can determine a worst case fault by assuming an infinite source. Simply take the full load amps of the transformer and divide by its per cent impedance (%Z).
dec_primary
New York
Electrical Engineer
Thanks Jim.
So to check my calcs, I would get 112.5kVA/208*sqrt(3) = 312.27 A (FLA) and then my AFC = 312.27A/.05 (assumption for now) which would land me at 6.25kA.
Making my breaker protecting the transformer a 10KAIC breaker. I'm assuming everything downstream of that is safe to size to the same KAIC value? My panel MCB and branch breakers also at 10KAIC?
When would I need to do a full short circuit study? Is that if this transformer was existing and I was planning on using it to add a panel?
Thanks Jim.
When you say "breaker protecting the transformer" is that on the primary or secondary side? If on the primary side, the AFC that sees would be based on the upstream transformer and conductor length.
jim dungar
Wisconsin
Thanks Jim.
Yes, your example is correct. Just be aware that transformers less than 500kVA often have impedances <5%.
Short circuit current does not get worse at downstream equipment unless there is another downstream source.
You should do a full short circuit study when the infinite bus method results are not satisfactory or when performing Arc Flash analyses.
dec_primary
New York
Electrical Engineer
Yeah, I meant on the primary side. Okay, so my calculation since my secondary voltage is 208V is for the AFC on the transformer secondary and so my panel main and branch circuits would be rated for 10kAIC. On the primary side, it looks like I'll have some digging to do and contact the utility because there's absolutely no information on the switch gear regarding the kAIC rating. Is that right?
dec_primary
New York
Electrical Engineer
Thank you. I just responded to the other comment regarding the primary vs secondary side of the transformer but now come to think of it...knowing what the utility transformer's impedance/voltage is is probably unnecessary because the voltage would be so much higher. So the worst case would indeed be the the secondary of my new transformer? Sorry for all the questions guys, but appreciate all the responses!
jim dungar
Wisconsin
Protective device AIC selection needs to be done separately for each side of the transformer.
Are you adding a new 480V protective device that will be feeding this new transformer? If you are you need to determine what AIC is needed based on the calculated fault current.
If you are using an existing protective device, how sure are you that its AIC was determined correctly? For example has the utility changed its transformer since the original service installation?
augie47
Tennessee
Definitely anecdotal but just to give you a ballpark number, the SCA on a couple of 112.5 kva I installed turned out to be in the 15-20k range.