I have a conduit coming from underground into the side of a Div II building.
The engineers drawing shows a seal just above the ground and then an LB into the Div II building. His classified area drawing shows the classifed area stopping at the building wall.
I question the LB fitting between the seal and the building. Ref 501.15-2 states "no fittings shall be between the seal and where the conduit leaves the boundary."
When it leaves the Div II area the LB is outside before turning underground through a seal.
Is this acceptable?
The engineers drawing shows a seal just above the ground and then an LB into the Div II building. His classified area drawing shows the classifed area stopping at the building wall.
I question the LB fitting between the seal and the building. Ref 501.15-2 states "no fittings shall be between the seal and where the conduit leaves the boundary."
When it leaves the Div II area the LB is outside before turning underground through a seal.
Is this acceptable?