Is a fixture tail considered a tap? What' determines what wires size the tail can be per code?..............
How about 12 awg thhn 20 amp circuit going to 4 square metal box then connecting (tapping) here onto 14 awg white romex to 4-0 plastic nail on box for lighting low 1.9 wat LED lamp? Would this be legal or considered a tap connection?It is not a tap, but "undersized" conductors are permitted between the branch circuit conductors and the fixture. See 240.5(B)(2) and make sure you note that this only applies to "fixture" wire of the types found in Table 402.3.
How about 12 awg thhn 20 amp circuit going to 4 square metal box then connecting (tapping) here onto 14 awg white romex to 4-0 plastic nail on box for lighting low 1.9 wat LED lamp? Would this be legal No or considered a tap connection? No
That would not be code compliant unless you have OCPD at 15 amps of less for the 14 AWG NM.How about 12 awg thhn 20 amp circuit going to 4 square metal box then connecting (tapping) here onto 14 awg white romex to 4-0 plastic nail on box for lighting low 1.9 wat LED lamp? Would this be legal or considered a tap connection?
I think the code doesn’t make much sense here as 14 NM has larger ampacity and protection than 16 - 18 AWG fixture wire but it’s code so I guess we’ll complyBefore jumping into using a fixture wire, however, be sure to note:
402.10 Uses Permitted. Fixture wires shall be permitted (1) for installation in luminaires and in similar equipment where enclosed or protected and not subject to bending or twisting in use, or (2) for connecting luminaires to the branchcircuit conductors supplying the luminaires.
402.12 Uses Not Permitted. Fixture wires shall not be used as branch-circuit conductors except as permitted elsewhere in this Code.
Yes interesting. I did look at the code and those codes referenced within this code. However, it still reads that the fixture conductor must be protected at its ampacity.That would not be code compliant unless you have OCPD at 15 amps of less for the 14 AWG NM.
However if you would use FMC and one of the conductors of the type shown in 402.3, you could use 18AWG for that installation and comply with the code.
Your statement is incorrect. You need to read 240.5 again especially 240.5(B) and (B)(2)Yes interesting. I did look at the code and those codes referenced within this code. However, it still reads that the fixture conductor must be protected at its ampacity.
Clearly the fixture wire ampacity is lower than the upstream 12 awg branch circuit.
For this reason I believe the code says to use supplementary overcurrent protection (for fixture wires) which can not replace main over current device.
How exactly do you install supplementary overcurrent protections downstream of main ocd breaker? Thanks never saw this done
Luminaire may also require 90C rated branch conductors, per 410.68It is not a tap, but "undersized" conductors are permitted between the branch circuit conductors and the fixture. See 240.5(B)(2) and make sure you note that this only applies to "fixture" wire of the types found in Table 402.3.
That's a common sense question. Unless the whip was factory installed and the light hasn't been modified in the field the wire is always gonna be smaller and sized according to the load of the device. Since none of us who actually do the work are authorized to put a ul sticker on our work. So just because a device is not passing a load through it and we know by common sense it will only draw the single amp or so of power it demands. We have to size wire according to the old, or rather vice versa. You can use bigger wire but never smaller.Is a fixture tail considered a tap? What' determines what wires size the tail can be per code?..............
Always viewed the fixture tail as the wiring provided via the factory wiring for connection between the mfg fixture and the building wiring of an individual light fixture. Typical residential wall or ceiling lights.A fixture tail is not required to be factory made or installed. As Don mentioned in post #8 a field made and installed tail of FMC and fixture wire would comply when using reduced size fixture wire conductors.
Going back to the OP the tail conductors would have to be suitable for the load and can be sized according to Table 402.5 and 240.5(B)(2).
Yes a lay-in style troffer fixture or a recessed high hat style fixture. When the wiring method is EMT above a suspended ceiling fixtures are typically feed by a fixture tail (or whip) with #18 fixture wires.Are you now speaking of or referring to a whip, typically installed on a trougher?
Never heard it called a tail.Yes a lay-in style troffer fixture or a recessed high hat style fixture. When the wiring method is EMT above a suspended ceiling fixtures are typically feed by a fixture tail (or whip) with #18 fixture wires.
That's what it's called around here. Outside of this forum I never hear it being called fixture whip.Never heard it called a tail.