Nickjungwirth1
New User
- Location
- Oregon
- Occupation
- Electrician
Ok, I have a FLA 75 amp portable heater on wheels 3 phase 480v. Im going to be feeding it off of an MCC to a 100 amp fused disconnect. RIght now I consider this a continuous load and thus needing to be x125 percent OCPD. so about 93 amps which would need a 100 amp bucket, My question is does this require the conductors from said MCC bucket to be sized at 125 percent as well?