Hi guys, maybe you can answer this problem and what was going on at this house.
Lady called and no power in a couple rooms. House is 50 years old. O.K. went over and checked the panel, handy man put 2 #12 on one 20 amp breaker, seen it before no big deal.
Well when I turned the 2 breakers on that were tripping they held for about 20 seconds and tripped both, one sp with one wire (which had nothing to do with the breaker that was losing power or tripping) it tripped first and then the other sp with 2 wires tripped about 5 seconds after the first one.
Took amp reading on all 3 wires and read maybe 1 amp on 2 of them and the third which was on the same breaker with another wire that had one amp and it read 53 amps. House is all gas.
Took the wire reading 53 amps and added a breaker to make it legal and it cleared everything and then read maybe one amp. Everything started working correctly and no problems since then.
Why was I reading 53 amps when it was on a sp breaker with another wire and then when I put it on its own breaker work fine.
They were not the same phase either.
Can someone tell me what was happening here.
Thanks for any feedback.
Lady called and no power in a couple rooms. House is 50 years old. O.K. went over and checked the panel, handy man put 2 #12 on one 20 amp breaker, seen it before no big deal.
Well when I turned the 2 breakers on that were tripping they held for about 20 seconds and tripped both, one sp with one wire (which had nothing to do with the breaker that was losing power or tripping) it tripped first and then the other sp with 2 wires tripped about 5 seconds after the first one.
Took amp reading on all 3 wires and read maybe 1 amp on 2 of them and the third which was on the same breaker with another wire that had one amp and it read 53 amps. House is all gas.
Took the wire reading 53 amps and added a breaker to make it legal and it cleared everything and then read maybe one amp. Everything started working correctly and no problems since then.
Why was I reading 53 amps when it was on a sp breaker with another wire and then when I put it on its own breaker work fine.
They were not the same phase either.
Can someone tell me what was happening here.
Thanks for any feedback.