augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Oct 8, 2015 #1 I have a new building, Class II Div 1, Group G . The owner has some old Class 1 Div 2 fixtures he wishes to install. My read is that it would be a violation..wrong classification, no group.... Correct ? (Fixture nameplate attached)
I have a new building, Class II Div 1, Group G . The owner has some old Class 1 Div 2 fixtures he wishes to install. My read is that it would be a violation..wrong classification, no group.... Correct ? (Fixture nameplate attached)
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Oct 8, 2015 #2 It would be a violation. See Section 500.8(B)&(C); especially, 500.8(B)(1).
K Kobe85 Member Location New York Oct 13, 2015 #3 are the new fixtures dual rated? In some cases they are.