So there is no 6 ft length limitation for your typical troffer whip (if using fixture wire)? Could have sworn that 6 ft thing was a thing, is there something else at play?
Unsupported lengths of flex six feet or less are allowed. If you want to go a hundred feet you're gonna have to spring for some straps.
Read 348.20 and 410.17 C carefully
Lot going on in in both those statements.
One discussion is conductor length and one is raceway type length.
When you combine both statements one could be lead astray.
Then go read 330.30 and be sure to read the last sentence after 330.30 (D) 3
Most are correct however do not get mislead as a whole. Each can be done after applying certain rules.
After review of above head on over to 402. Read slowly as you get to 402.5 - 402.12. stop and think after 402.7.
Then after 402.12 head on over to 240.5.
Then it should clear thing up a little.
I base this on 2017 code for previous OP saying he is on 2017 NEC
For fun have. A look at 310.10.
I would say type TFN and TFFN are dry location only no damp.
A lot of lay in fixtures are damp location listed. See 402.2
IFN sends you to 410.52 and then back agai
Lot going on in a simple question.
Each type of install requires different methods to meet NEC.
A lot of contractors today "daisy chain" their troffer fixtures. If you do this, you can't use the factory pre-made fixture whips unless the conductors have an ampacity of 20 amps. For example, if you daisy chained 30 troffers together, the whip between fixture #1 and #2 will see the load of the other 29 fixtures. I used to do this often because if your whips are 6' or less, Art. 330.30 (D)(2) allow you to run the whips unsupported which will save you lot of work not having to install your own ceiling wires.
So I have a Question
TFN and TFFN is dry location only?
I see it as a yes. Some lay in fixtures are damp location listed as well as other luminaries. So the application of a whip and or whip type should be chosen wisely.
Back to 348 and the use of a THHN/THWN conductor. This would require a branch circuit size if used in a damp location. Another item is it is allowed to be concealed. It would also be allowed to installed unsupported and secured if 6' or less. For this discussion 348.30 exception 4 accessable ceiling.
Just some thought on the issue.