The Iceman
Senior Member
- Location
- Florida
I have a question about the 18 gauge fluorecsent fixture wips that come from the manufacturer. I don't understand why we can't use them to wire up more than one fixture? According to NEC 2005, Table 402.5, allowable ampacity for fixture wires, 18 gauge is good for 6 amps. Article 240.5 (B) (2) (1), if my overcurrent protection device is 20A, and I tap off a branch circuit with a fixture wire not more than 50', 18 gauge is ok. If each fluorecsent fixture wip is 18 gauge, and each fixture is 1A, can't I use that wip to wire up 6 fixtures? Am I missing an article in the NEC that prohibits this, or is it the manufacturers specifications? Any help would be greatly appreciated.