FWIW, I have an area of a couple of square feet above my shower which is denuded of the "popcorn" ceiling texture from when the shower head developed a leak and sprayed the ceiling. I'm just sayin'...2 - I have a recessed light installed in a tub/shower (no hand held). Open trim rated for damp location. Inspector claims this ceiling is a wet location as it is subject to shower spray. I disagree. The shower spray can not hit the ceiling. It is unlikley that the spray would bounce off a body and hit the ceiling also......... but that's not shower spray anyways!
If not with a handheld when would it be?:huh:
When you try to save $30 bucks and try to give the dog a bath yourself.![]()
Violation # 1: No GFCI rated receptacle required unless
within 6 ft. of a water source......The washing machine
potable water supply line would not qualify as a valid
"water source".
Violation # 2: IMO, ...yes, a "wet rated" fixture should
have been installed......The "What If" Factor is a valid one!
This same line of thought is used on GFCI rated
receptacles all the time, ...as long as no one touches an
ungrounded conductor / surface, ...no harm & no damage.
"What If" someone touches an ungrounded conductor /
surface ?
Luminaires located within the actual outside dimension of the bathtub or shower to a height of 2.5 m (8 ft) vertically from the top of the bathtub rim or shower threshold shall be marked for damp locations, or marked for wet locations where subject to shower spray.
AFCI or GFCI?I think a shower trim would have been the wise choice there.
The gfci, as stated, is required within 6' of the sink-- be ready 2014- afci in the laundry room.
Possibly both. AFCI yes and GFCI if within 6' of a sink-- but that is 2014 NECAFCI or GFCI?
Violation # 1:
From the `06 IRC, Section E3802.7, ...from the`08 NEC,
Artcle 210.8(A)(7).